Sorry in advance as I know this has been beat to death, but I have multiple instances of small 480-208Y/120V xfmrs in a concrete/wood fame industrial building with nothing to ground to (no steel or water pipe). Inspector wants a GEC routed back to the service rather than driving a local rod per 250.30 (7) Exception #1 and 250.52 (A)(5). The service is up to 300ft away in some cases. Do you agree that this is the best solution? Since the CMP can't agree on the dual use (EGC/GEC) of an upsized feeder EGC I don't plan to pursue that avenue.