B Bill_From_GA Member Mar 27, 2018 #1 338.12 does not allow SE cable to be placed in underground conduit. It also does not allow USE cable inside a dwelling. What do you use to go from underground to an inside panel?
338.12 does not allow SE cable to be placed in underground conduit. It also does not allow USE cable inside a dwelling. What do you use to go from underground to an inside panel?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Mar 27, 2018 #2 You use dual rated underground conductor, RHW/USE or something similar.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 27, 2018 #3 THWN-2 or XHHW-2 would be my choice.