I'm a little confused on the amp rating of SE cable. I have been installing this for electric furnaces for as long as I can remember. I have been installing it under the 2008 NEC. When I look at
338.10 (b)(4)(a) for interior installations it says that I must comply with part II of article 334. In that part it says that it must use the 60 degree column for ampacity. If I look at that column it says it is only good for 55 amps, yet I have been using it for furnaces that draw 55-59 amps all the time and never get tagged for it. I always assumed it was good for 65 amps and I could use the 75 degree column. I thought it was weird that in 2011 a code change said that this wires ampacity now had to be determined by the 60 degree column. Wasn't it always in the 60 degree column if it has always had to comply with part II of article 334?
The wire I use is SE cable U type THHN
338.10 (b)(4)(a) for interior installations it says that I must comply with part II of article 334. In that part it says that it must use the 60 degree column for ampacity. If I look at that column it says it is only good for 55 amps, yet I have been using it for furnaces that draw 55-59 amps all the time and never get tagged for it. I always assumed it was good for 65 amps and I could use the 75 degree column. I thought it was weird that in 2011 a code change said that this wires ampacity now had to be determined by the 60 degree column. Wasn't it always in the 60 degree column if it has always had to comply with part II of article 334?
The wire I use is SE cable U type THHN