For the 2014 NEC, I would think you'd want to install a barrier (1x running board?) between the SE cable and the top of the loose fiberglass so that the cable is not "in" the insulation. The relevant texts:
2014 338.10(4)(a) in part:
Where installed in thermal insulation, the ampacity shall be in accordance with 60°C (140°F) conductor temperature rating. The maximum conductor temperature rating shall be permitted to be used for ampacity adjustment and correction purposes, if the final derated ampacity does not exceed that
for a 60°C (140°F) rated conductor.
2017 338.10(4)(a) in part:
For Type SE cable with ungrounded conductor sizes 10 AWG and smaller, where installed in thermal insulation, the ampacity shall be in accordance with 60°C (140°F) conductor temperature rating. The maximum conductor temperature rating shall be permitted to be used for ampacity adjustment and correction purposes, if the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor
Cheers, Wayne