74sparks
Member
- Location
- Pennsylvania
- Occupation
- Electrical Engineer
338.10(B)(4)(a)(1) states "Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of part II of Article 334, excluding 334.80.
Of course 334.80 is the Ampacity clause, stating we shall never exceed that of a 60°C rated conductor.
So, if an SE cable is marked 75°C, is that the ampacity one would use for installing it as a feeder in an unfinished basement? If not, I'm seeing no benefit to even considering SE, as going to 60°C rating on it actually pushes the cost above NM-B.
In this case, I'm evaluating a 50A feeder, the SE (or NM-B AWG-6/3+G) comprising a run from breaker to junction with THWN-2 at AWG-8.
Of course 334.80 is the Ampacity clause, stating we shall never exceed that of a 60°C rated conductor.
So, if an SE cable is marked 75°C, is that the ampacity one would use for installing it as a feeder in an unfinished basement? If not, I'm seeing no benefit to even considering SE, as going to 60°C rating on it actually pushes the cost above NM-B.
In this case, I'm evaluating a 50A feeder, the SE (or NM-B AWG-6/3+G) comprising a run from breaker to junction with THWN-2 at AWG-8.