What type of mast was this for . Primary power? secondary power.? if RES sendary power I might know.
If the SE overhead cable was exposed then yes it would fail. Even though you terminated in box, that seems ok. but when se cable is exposed such as USE, it will fail the inspection because of the insulation rating of the cable. If you used USE-2 it would have passed or even TYPE-U with XHHW would pass. I Just did a service not to long ago and double checked this with the AHJ and he told me that USE would fail my install because it would be exposed more than 3 ft. coming out of the riser because of the insulation rating. some AHJ will approve it some will not thats up to them. but USE-2 would pass. again because of the insulation rating . FIre, Sunlight, etc, USE does not have one of the rating that USE-2 does and Type-U XHHW thats what fails it. I had this written down on the insulations of these conductors.but you might want to check the NEC it has in their
I just dumped the USE all togeather and went with TRI-Plex direct burial saves me trouble and time and I pass .. whoope.!