SE Cable Prohibited for use in overhead services?

Status
Not open for further replies.
Please excuse me if this seems like a dumb question? Is SE cable no longer allowed for residential overhead services? Every search I have conducted on the internet indicates only conduit can now be used.
 
Please excuse me if this seems like a dumb question? Is SE cable no longer allowed for residential overhead services? Every search I have conducted on the internet indicates only conduit can now be used.

Se cable can still be used unless your area prohibits it.
 
Please excuse me if this seems like a dumb question? Is SE cable no longer allowed for residential overhead services? Every search I have conducted on the internet indicates only conduit can now be used.

False. In fact you can even use it for commercial services if you want. There are however various local prohibitions against it across the US, either because of a direct restriction, or perhaps an interpretation of "physical damage". Washington state does not allow SE for services.
 
The NEC still allows it even under the 2017. Around here about 90% of all overhead residential services are done with SE cable.
 
Please excuse me if this seems like a dumb question? Is SE cable no longer allowed for residential overhead services? Every search I have conducted on the internet indicates only conduit can now be used.

Just out of curiosity what search results brought you to this conclusion?
 
The rules in PG&E'S Greenbook do not allow SE cable to be used, the NEC does, but PG&E wins because if they don't like it, it won't get connected. Have been told that SCE, Southern California Edison rules are the same, those who work in SCE territory can confirm or deny it.
 