SE Cable Protection entering a plastic 1 gang box

Status
Not open for further replies.

Duncan8943

Member
Location
Lexington
I'm running SE cable from the panel to a 1G plastic box with knock outs. According to 314.17, I need to secure the cable within 8" of the box. Since my cable is 2-2-2-4 SE cable, I also have to go by 300.4(G)--which is for insulated fittings. If I staple/strap the wire within 8" of the 1 gang box and go through a male adapter with a locknut and plastic bushing--Is this acceptable? How about using a box connector with a coupling instead?
 
lul wut?

Have you checked the wirefill on that single gang box? Pretty sure your over a little.

Are you trolling? Seriously if you are I don't judge.
 