The 2008 code has deleted the reference for excluding the temp ampacity in 334.80 for SE cable. According to the 2008 code article 338.10(B)(4), SE cable installed as branch circuit or feeders must use the 60 degree ampacity column for interior wiring according to part II of article 334 which includes 334.80. Most code update books do not even recognize this change. Did anyone notice this change? This will require many SE cable installations to be upsized.