I noticed a change in article 338 (SE cable)
338.10(B)(4)(a) interior instalations In addition to the provisions of this article, Type SE service entrance cable used for interior wiring shall comply with the instalation requirements of Parts I and II of article 334, excluding 334.80
This is the text from the '05. The parts in red are deleted in the '08 NEC. Part I in 334 is definitions, so that doesn't really affect anything. However 334.80 is the section that restricts the ampacity of NM to the 60? column.
I guess that we can no longer use the 75? column when using SE cable for feeders and circuits, which was a reason for using this instead of romex.
338.10(B)(4)(a) interior instalations In addition to the provisions of this article, Type SE service entrance cable used for interior wiring shall comply with the instalation requirements of Parts I and II of article 334, excluding 334.80
This is the text from the '05. The parts in red are deleted in the '08 NEC. Part I in 334 is definitions, so that doesn't really affect anything. However 334.80 is the section that restricts the ampacity of NM to the 60? column.
I guess that we can no longer use the 75? column when using SE cable for feeders and circuits, which was a reason for using this instead of romex.