SE Cable

Status
Not open for further replies.

saulsteam

Member
Location
California
Can SE cable be installed exposed in a crawl space/basement on a single family home when the cable is above 7' and run in line with the girder members that support the floor system from the meter to the panel?
Thanks

Inspector quoted 230.50 B and 300.4
 
Is this ser or seu cable. Sounds to me like this is a feeder in which case 230 does not apply.


The section below is for nm cable but section 338.10(B)(4) sends us to article 334.

334.15(C) In Unfinished Basements and Crawl Spaces. Where cable
is run at angles with joists in unfinished basements and crawl
spaces, it shall be permissible to secure cables not smaller than
two 6 AWG or three 8 AWG conductors directly to the lower
edges of the joists. Smaller cables shall be run either through
bored holes in joists or on running boards. Nonmetallicsheathed
cable installed on the wall of an unfinished basement
shall be permitted to be installed in a listed conduit or tubing
or shall be protected in accordance with 300.4. Conduit or
tubing shall be provided with a suitable insulating bushing or
adapter at the point the cable enters the raceway. The sheath of
the nonmetallic-sheathed cable shall extend through the
conduit or tubing and into the outlet or device box not less
than 6 mm (1∕4 in.). The cable shall be secured within 300 mm
(12 in.) of the point where the cable enters the conduit or
tubing. Metal conduit, tubing, and metal outlet boxes shall be
connected to an equipment grounding conductor complying
with the provisions of 250.86 and 250.148.


334.10(B)(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions of
this article, Type SE service-entrance cable used for interior
wiring shall comply with the installation requirements of Part II
of Article 334, excluding 334.80.
 