I am somewhat confused.
338.10B(4)a Tells me that for interior installations SE cable must comply with part 2 of 334. Under 334.80 NM ampacity shall be in accordance with 60 degree temp rating. This would say that interior se and nm shall be sized to the 60 degree column of table 310.16
Massachusetts amends 334.80 as follows...
Delete the second paragraph and revise the first paragraph to read as follows:
334.80 Ampacity Type NM, NMC, and NMS cable shall have conductors rated at 90c. Where installed in thermal insulation, the ampacity of conductors shall be that of 60c conductors.
So with that amendment, if SE or NM is not installed in thermal insulation I would size according to the terminal rating of the equipment I am connecting to. I believe that in most cases this would be a 75c rating therefore #8 NM can be protected at 50 amps.
Also for a 100 amp sub panel I would have to use #1 AL sized at 75c
Am I off track here?
338.10B(4)a Tells me that for interior installations SE cable must comply with part 2 of 334. Under 334.80 NM ampacity shall be in accordance with 60 degree temp rating. This would say that interior se and nm shall be sized to the 60 degree column of table 310.16
Massachusetts amends 334.80 as follows...
Delete the second paragraph and revise the first paragraph to read as follows:
334.80 Ampacity Type NM, NMC, and NMS cable shall have conductors rated at 90c. Where installed in thermal insulation, the ampacity of conductors shall be that of 60c conductors.
So with that amendment, if SE or NM is not installed in thermal insulation I would size according to the terminal rating of the equipment I am connecting to. I believe that in most cases this would be a 75c rating therefore #8 NM can be protected at 50 amps.
Also for a 100 amp sub panel I would have to use #1 AL sized at 75c
Am I off track here?