iwire
from an earlier thread (now closed) you posted:
from an earlier thread (now closed) you posted:
I believe it actally says:If this circuit is SE cable 338.10(B)(4)(a) requires us to use parts I and II of 334 which includes 334.80s 60 C requirement.
Does this not mean the 75o rating would be acceptable?(4) Installation Methods for Branch Circuits and Feeders
(a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Parts I and II of Article 334, excluding 334.80 .