I've been reading the NEC as well as a handful of threads on this forum about using SE type R cable for feeder. I still cant figure out what the verdict is.
I have to move a meter enclosure about 30' away from the house load center as well as upgrading to a 200A load center. In doing so I have added a 200A main disconnect next to the meter enclosure. From the main disconnect (now my ground bonded panel) I am looking to run SE type R to the 200A load center. using 4/0-4/0-4/0-2/0 AL loose in the attic save for 4 feet in raceway to go from the panel into the attic. This city follows NEC2011.
I am looking at table 310.15(B)(7) which makes it seem acceptable but then see references to using the 60c column of table 310.15(B)(16) which makes it seem not ok.
I have to move a meter enclosure about 30' away from the house load center as well as upgrading to a 200A load center. In doing so I have added a 200A main disconnect next to the meter enclosure. From the main disconnect (now my ground bonded panel) I am looking to run SE type R to the 200A load center. using 4/0-4/0-4/0-2/0 AL loose in the attic save for 4 feet in raceway to go from the panel into the attic. This city follows NEC2011.