I said, "let's not put the site lighting pole in the C1D2 hazardous location". "Jump off a bridge", was the reply.
So here we go.
Pole is 30' tall and located in a C1D2 hazardous location due to LNG/methane process. The hazardous/nonhazardous boundary is 15 ft radious from source horizontal and above grade. The pole is a standard hollow pole with a handhole. The light fixtures are factory sealed but mounted outside the hazardous boundary. The wiring is standard THWN building wire and is not a cable.
I am suggesting installing the RGS conduit has to be run on the outside of the pole. LFMC will complete the connection to the fixtures. Install one boundary seal within 10 ft of grade and a second boundary seal between 5 ft and 25 ft above grade. 501.15(B)(2) Exception No. 4 aieliminating the second seal is ALMOST satisfied but condition (4) is not met. The overlap presents a bit of a Code mind-bending but I think it is compliant.
Further I am suggesting wiring ran inside the pole would not be Code permitted because it is not a listed wiring method. the elevated second boundary seal would be beyond 10 ft of the boundary.
Am I wrong?
So here we go.
Pole is 30' tall and located in a C1D2 hazardous location due to LNG/methane process. The hazardous/nonhazardous boundary is 15 ft radious from source horizontal and above grade. The pole is a standard hollow pole with a handhole. The light fixtures are factory sealed but mounted outside the hazardous boundary. The wiring is standard THWN building wire and is not a cable.
I am suggesting installing the RGS conduit has to be run on the outside of the pole. LFMC will complete the connection to the fixtures. Install one boundary seal within 10 ft of grade and a second boundary seal between 5 ft and 25 ft above grade. 501.15(B)(2) Exception No. 4 aieliminating the second seal is ALMOST satisfied but condition (4) is not met. The overlap presents a bit of a Code mind-bending but I think it is compliant.
Further I am suggesting wiring ran inside the pole would not be Code permitted because it is not a listed wiring method. the elevated second boundary seal would be beyond 10 ft of the boundary.
Am I wrong?