Hi,
I have two questions with regrads sealing off conduits in hangar space that i'm confuse with and any help will be appreciated:
1. My understanding is that the hangar space in many location is classified as Class 1 Div 2 if it was below 18”. If equipment or devices (receptacles) that are located higher than 18”, is a seal off (EYS fitting) still required even though the devices (receptacles or switches) or equipment are not explosion proof?
2. If a seal off is provided at the hangar space, is a second seal off also will be required in the electrical room that is located in unclassified area?
Thanks in advance,
I have two questions with regrads sealing off conduits in hangar space that i'm confuse with and any help will be appreciated:
1. My understanding is that the hangar space in many location is classified as Class 1 Div 2 if it was below 18”. If equipment or devices (receptacles) that are located higher than 18”, is a seal off (EYS fitting) still required even though the devices (receptacles or switches) or equipment are not explosion proof?