14-34 Log #2937 NEC-P14
(501-5(B)(2))
Final Action: Accept in Principle
Submitter: Dorothy Kellogg, American Chemistry Council
Recommendation:
At the end of the requirement add a sentence to read:
Sealing fittings shall not be required to be explosion proof.
Substantiation:
Seals in conduits passing from Division 2 locations into unclassified locations are needed to prevent the passage of gases or vapors,
not to contain explosions in the conduit system as is the case with Division 1 conduit systems. This proposal will allow same type seals
as permitted in 504.70 for intrinsic safe installations. The existing text (501.5(B)(2)) eludes to this: "sealing fitting...shall be designed
and installed so as to minimize the amount of gas or vapor within the Division 2 portion of the conduit from being communicated to the
conduit beyond the seal". However, it is now common practice to require explosion proof seals. Explosion proof seals are expensive and
make it difficult to modify wiring once installed. This proposal will make it clear that explosion proof seals are not required as
boundary seals between Division 2 and unclassified locations.
Panel Meeting Action: Accept in Principle
Revise 501.5(B)(2) to read as follows:
"(2) Class I, Division 2 Boundary. In each conduit run passing from a Class I, Division 2 location into an unclassified location, the
sealing fitting shall be permitted on either side of the boundary of such location within 3.05 m (10 ft) of the boundary and shall be
designed and installed so as to minimize the amount of gas or vapor within the Division 2 portion of the conduit from being
communicated to the conduit beyond the seal. Rigid metal conduit or threaded steel intermediate metal conduit shall be used between
the sealing fitting and the point at which the conduit leaves the Division 2 location, and a threaded connection shall be used at the
sealing fitting. Except for listed explosionproof reducers at the conduit seal, there shall be no union, coupling, box, or fitting between
the conduit seal and the point at which the conduit leaves the Division 2 location. Conduits shall be sealed to minimize passage of gases
or vapors within the Division 2 portion of the conduit from being communicated to the conduit beyond the seal. Such seals shall not be
required to be explosionproof."
Panel Statement:
CMP 14 agrees with the submitter but believes that the language used in 504.70 provides greater clarification.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 13 Negative: 1
Explanation of Negative:
COOK: I agree with the first sentence of the submitter's substantiation. I do not agree with the proposed text or the referenced text in
504.70. The text provides no guidance for installers or inspectors as to what is an acceptable seal. Almost anything would have some
affect on gas or vapor passing through a conduit; rags, caulk, silicone, wax, plumbers putty, a four bend saddle in the conduit with water
collected like a plumbing trap, bubble gum, but which ones would "minimize" the passage of the gases? If paper towels are used, do you
need one or two of them to minimize the passage of gas? If caulk or silicone is used, would the installer or inspector know the affect of
the material on conductor insulation? Would conduits that depend on a single compression seal to prevent flammable liquids from
entering the conduit system be safe with bubble gum as a boundary seal (see 501.5(B)(2), Exception No. 4)?
I believe the proposed text will result in inconsistent installations, inconsistent inspections and certainly inconsistent interpretations
of the requirement. Until clear text is proposed, that is enforceable; I will not support this change. I agree that a Division 2 to
unclassified location, boundary seal does not need to be explosionproof, but I am not aware of a seal that is manufactured and listed to
minimize the passage of gas or vapor that is not also explosionproof.
Comment on Affirmative:
WECHSLER: In taking the action that likely will satisfy the proposal, the Panel should also consider making some
other editorial revisions to eliminate the phrase following the subsection title so that a complete sentence exists.
This phrase resulted from the revision that was made during the last code cycle, when this phrase was the lead-in
for the paragraph. The following is offered for consideration:
Revise 501.5(B)(2) additionally to read as follows:
(2) Class I, Division 2 Boundary. So as to minimize the amount of gas or vapor within the Division 2 portion of the
conduit from being communicated to the conduit beyond the seal, a sealing fitting shall be installed in In each conduit
run passing from a Class I, Division 2 location into an unclassified location., the The sealing fitting shall be
permitted on either side of the boundary of such location within 3.05 m (10 ft) of the boundary. and shall be
designed and installed so as to minimize the amount of gas or vapor within the Division 2 portion of the conduit from
being communicated to the conduit beyond the seal. Rigid metal conduit or threaded steel intermediate metal conduit
shall be used between the sealing fitting and the point at which the conduit leaves the Division 2 location, and a
threaded connection shall be used at the sealing fitting. Except for listed explosionproof reducers at the conduit
seal, there shall be no union, coupling, box, or fitting between the conduit seal and the point at which the conduit
leaves the Division 2 location. Conduits shall be sealed to minimize passage of gases or vapors within the Division 2
portion of the conduit from being communicated to the conduit beyond the seal. Such seals shall not be required to be
explosionproof.
1238