This is a sewer plant .Just where do we need to place seal offs. The engineer wants them at each piece of equipment. Plus just before we go thru the wall??
If the wall is the Class I Division 1 boundary, and the conduit run extends beyond the boundary, then under the NEC a seal off is required within 10 ft either side with no fittings between boundary and seal off except for XP reducers in the seal off hub.This is a sewer plant .Just where do we need to place seal offs. The engineer wants them at each piece of equipment. Plus just before we go thru the wall??