is a seal off required in a air supply house when a conduit passes thru a wall and there is a temperature change that the conduit will see to prevent condensation froming within the conduit and tracking back into the control panels?
 
Yes, but not an explosionproof type fitting.

(A) Sealing. Where portions of a raceway or sleeve are
known to be subjected to different temperatures, and where
condensation is known to be a problem, as in cold storage
areas of buildings or where passing from the interior to the
exterior of a building, the raceway or sleeve shall be filled
with an approved material to prevent the circulation of
warm air to a colder section of the raceway or sleeve. An
explosionproof seal shall not be required for this purpose.
 
is a seal off required in a air supply house when a conduit passes thru a wall and there is a temperature change that the conduit will see to prevent condensation froming within the conduit and tracking back into the control panels?

I found it...300.7

Seal off not required but the conduit shall be sealed. Duct seal should do the job.
 