randy riley said:
can sealtight be use in hazardous locations as in fual areas?

It can be used in Class 1 Div 2 under some conditions, but it cannot be used in Class 1 Div 1. If you're talking about any fuel dispensing station like bulk tanks on a farm or something at least a small area around the tanks will be Class 1 Div 1. Sorry I don't have code references, I'm at home and my NEC is at work.
 

frizbeedog

Senior Member
Location
Oregon
randy riley said:
can sealtight be use in hazardous locations as in fual areas?

350.10 Uses Permitted

2008

This will refer you to the additional articles for it's use and restrictions, for the location you describe.
 