Can feeder cables from an outside generator be ran in seal-tight to a point of entry to a house?
 
Re: Seal-tight

I don't know the exact application but as long as it is supported every 4.5 feet and 12" from each termination and the Liquid tite is rated for UV if outdoors you should be ok.
 
Re: Seal-tight

I did this, using a 60-amp AC disconnect at the point of entrance, and it looks like a typical AC installation. I used paired Mineralacs to attach the Sealtite to the gas line. (The inspector didn't mention the pipe support.)
 