Is the question "must all PVC in use be underground?" or is it "must all underground wiring be in PVC?"lddd340 said:What I have read is 348.12 that covers FMC. This is just regular seal tite that is under the ground. You do not have to use PVC under ground at all times?????
LFMC-350.10 Uses Permitted.
LFMC shall be permitted to be used in exposed or concealed locations as follows:
(1) Where conditions of installation, operation, or maintenance require flexibility or protection from liquids, vapors, or solids
(2) As permitted by 501.10(B), 502.10, 503.10, and 504.20 and in other hazardous (classified) locations where specifically approved, and by 553.7(B)
(3) For direct burial where listed and marked for the purpose
lddd340 said:It was 350 that was used
lddd340 said:It was 350 that was used, I do not have a code book here. I know that it was regular seal tite so I do not know if it can go in the ground? If it can go through aggregate? It is not marked that it can be place under ground.
peter d said:In my opinion, metallic seal tight is garbage.