kingpb
Senior Member
- Location
- SE USA as far as you can go
- Occupation
- Engineer, Registered
The contractor is proposing to use only firestop expandable foam to seal cable penetrations into a GE PEECC; otherwise known as a manufactured electrical house (building). The building is outdoor and the penetrations are from cables underneath in cable tray. We were expecting cable glands and gland plates but the contractor is saying the foam is an acceptable method.
All the firestop foam I can find online says it's not water tight, or UV so they intend on covering it with, well, essentially caulk to waterproof it. I have said this is not adequate per NEC 110.12 and referred to ANSI/NECA 1-2015.
Looking for input on options/comments for sealing properly.
All the firestop foam I can find online says it's not water tight, or UV so they intend on covering it with, well, essentially caulk to waterproof it. I have said this is not adequate per NEC 110.12 and referred to ANSI/NECA 1-2015.
Looking for input on options/comments for sealing properly.