I notice in my area it appears that the 'sealant' that is to be installed inside conduit to help prevent water and condensation when entering buildings from outside because of temperatures is not enforced or forgotten. NEC 2020 300.7
Recently had a complaint about a water leaking from conduit in a tele data room. Conduit comes though building from outside (LB on other side of wall) and was full of water. No sealant. other conduit run just ran straight through, no c, lb etc.. close to the entry point to put a sealant.
Do inspectors in anyone elses area look for a 'c , LB , box, etc.. on the other side of the wall when conduit is coming from inside to outside that would show proof there is sealant in pipe? Suprisingly, it appears that some electricians forget about it alot.
Recently had a complaint about a water leaking from conduit in a tele data room. Conduit comes though building from outside (LB on other side of wall) and was full of water. No sealant. other conduit run just ran straight through, no c, lb etc.. close to the entry point to put a sealant.
Do inspectors in anyone elses area look for a 'c , LB , box, etc.. on the other side of the wall when conduit is coming from inside to outside that would show proof there is sealant in pipe? Suprisingly, it appears that some electricians forget about it alot.