Sealing Fittings for Cables in Class 1 Division 2 Location

Merry Christmas

timm333

Senior Member
Location
Minneapolis, MN
Occupation
Electrical Design Engineer
I am trying to figure out whether sealing fittings are required for multiconductor cables in class 1 division 2 location. Cables have gas/vapor tight sheaths, but they are still capable of transmitting gases/vapors through the cable core. The enclosure in which these cables will be terminated does not have to be explosion proof, because it does not have any arcing or heat producing device in it.

NEC 501.15(E)(3) states that cables shall not be required to be sealed unless required by 501.15(E)(1). NEC 501.15(E)(1) states that cable seals are required when the enclosure is required to be explosionproof. But it also says that multiconductor cables, whose core can transmit gases/vapors, will require to be sealed.

Maybe there is possibility that if cables are not sealed, then flammable gases/vapors might travel through the cable core and enter into the control room on the other end.

Are cables required to be sealed even if the enclosure does not have to be explosionproof, or can we just install explosionproof glands (suitable for class 1 division 2) on the cables? What do you guys think about it? Thanks.
 
"Maybe there is possibility that if cables are not sealed, then flammable gases/vapors might travel through the cable core and enter into the control room on the other end."

If you are wiring from a non-hazardous control room to a division 2 hazardous space, wouldn't you need a seal regardless?
 
"Maybe there is possibility that if cables are not sealed, then flammable gases/vapors might travel through the cable core and enter into the control room on the other end." If you are wiring from a non-hazardous control room to a division 2 hazardous space, wouldn't you need a seal regardless?


No. Because these cables are in cable tray (not in conduits). So if cables were suitable for class 1 division 2 (like TC/tray cable) then there would be no need to place seals at the boundary where cables transition from non-hazardous to hazardous location. But the issue here is that the cables are not rated for class 1 division 2. The outer sheaths of cables are gas/vapor tight, but gas/vapor can still travel through the core of cables. I think seals would be required; but just thought to see if you guys have some other idea.
 
No. Because these cables are in cable tray (not in conduits). So if cables were suitable for class 1 division 2 (like TC/tray cable) then there would be no need to place seals at the boundary where cables transition from non-hazardous to hazardous location. But the issue here is that the cables are not rated for class 1 division 2. The outer sheaths of cables are gas/vapor tight, but gas/vapor can still travel through the core of cables. I think seals would be required; but just thought to see if you guys have some other idea.
MC-HL and teck cable are required to be sealed if going from control room to classified area.

The cable inside may need a gas block kit as well.

Not sure what else you could be using that wouldn’t require a seal of some sort, at least a Roxblox cut out.
 