- Location
- Illinois
- Occupation
- retired electrician
We have EMT conduits containing intrinsically safe circuits leaving a Class I, Division 1 area and entering a sealed control room with no openings between the room and the classified area other than the raceways. The personnel door opens to an unclassified area. 504.70 kind of says we do not need an explosion proof seals, and it appears that we don't need a "sealing fitting" but can use seal the conduit itself with a product that is identified for the purpose of minimizing the passage of gasses and vapors.
The language in 504.70 is not completed clear as it references 501.15 and the boundary between a Division 1 location and a non-classifed location requires a seal and sealing compound. That seems to conflict with the last part of 504.70 that says an explosion proof seal is not required.
Just looking for other opinions. I am leaning towards the idea that as long as we use a product to that is identified for the purposes of minimizing the passage of vapors and gasses in the conduit at the boundary we will be complying with the intent of the code.
We are looking as using PolyWater FST Duct Sealant for this. The manufacturer's information says the product meets the following code requirement:
The language in 504.70 is not completed clear as it references 501.15 and the boundary between a Division 1 location and a non-classifed location requires a seal and sealing compound. That seems to conflict with the last part of 504.70 that says an explosion proof seal is not required.
Just looking for other opinions. I am leaning towards the idea that as long as we use a product to that is identified for the purposes of minimizing the passage of vapors and gasses in the conduit at the boundary we will be complying with the intent of the code.
We are looking as using PolyWater FST Duct Sealant for this. The manufacturer's information says the product meets the following code requirement:
NEC 501.15(B)(2) Conduit Seals, Class 1 Division 2: A conduit seal shall be required in each conduit run leaving a Class 1, Division 2 location... and it shall be designed and installed tominimize the amount of gas or vapor within the portion of the conduit installed in the Division 2 location... Such seals shall not be required to be explosion proof...