SceneryDriver
Senior Member
- Location
- NJ
- Occupation
- Electrical and Automation Designer
Two scenarios:
1) I'm exiting a 3R disconnect through the factory-supplied concentric KO's at the bottom. Do I need sealing locknuts on these fittings? I don't believe so, since I will be below all live parts. A wire-type EGC will be pulled through these conduits. The opposite end of the conduits will be in field-punched KO's in metal enclosures. The EGC will terminate in those enclosures on appropriate lugs. These will be feeder (fused) conductors and so will not need bonding bushings, as the conductors are OC protected and L-to-G voltage is 120V, yes?
2) I'm entering the same disconnect through a field-punched KO on the side, down low (bottom corner), below all live parts. I do need raintight EMT fittings, or a rigid nipple with a sealing locknuts on the outside. These will be service (unfused) conductors from the adjacent meter, and will need a bonding bushing with a lay-in lug on at least one side, yes?
Thanks,
SceneryDriver
1) I'm exiting a 3R disconnect through the factory-supplied concentric KO's at the bottom. Do I need sealing locknuts on these fittings? I don't believe so, since I will be below all live parts. A wire-type EGC will be pulled through these conduits. The opposite end of the conduits will be in field-punched KO's in metal enclosures. The EGC will terminate in those enclosures on appropriate lugs. These will be feeder (fused) conductors and so will not need bonding bushings, as the conductors are OC protected and L-to-G voltage is 120V, yes?
2) I'm entering the same disconnect through a field-punched KO on the side, down low (bottom corner), below all live parts. I do need raintight EMT fittings, or a rigid nipple with a sealing locknuts on the outside. These will be service (unfused) conductors from the adjacent meter, and will need a bonding bushing with a lay-in lug on at least one side, yes?
Thanks,
SceneryDriver