Sealing locknuts?

Status
Not open for further replies.

veco

Member
Does the use of sealing locknut(s) on rigid conduit qualify as "dust tight" (NEMA12) if the UL compliance stated for the locknut is "liquid tight". If so, where can I find something stating that "liquid tight" trumps "dust tight"?
 

veco

Member
Thanks for the assist, but I'm still confused. UL lists certain sealing locknuts as compliant to 514B (liquid tight) but nowhere can I find "dust tight", which is a defining feature of NEMA12. Common sense says liquid tight implies inclusion of dust tight, but I can't find it in writing. I guess a UL inspector would have to decline approval of a penetration into a NEMA12 enclosure by a conduit that is liquid tight sealed by a sealing locknut, Huh?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
veco said:
Thanks for the assist, but I'm still confused. UL lists certain sealing locknuts as compliant to 514B (liquid tight) but nowhere can I find "dust tight", which is a defining feature of NEMA12. Common sense says liquid tight implies inclusion of dust tight, but I can't find it in writing. I guess a UL inspector would have to decline approval of a penetration into a NEMA12 enclosure by a conduit that is liquid tight sealed by a sealing locknut, Huh?

Sealing Locknut
141.gif


Here is what I found. A sealing locknut is a Nema FB-1 standard. You need to figure out what class and division you have because the following red statement will tell you what areas are excluded from this standard.

[FONT=Verdana,Arial]FB 1-2007 covers fittings that are a part of electrical raceway systems and meet requirements of the National Electrical Code? (NEC). These include fittings used with non-flexible tubular raceways, as well as flexible conduit and cable raceways that encompass flexible metal conduits, armored cable, metal-clad cable, tray cable, mineral-insulated cable, flexible cords, nonmetallic sheathed cable, and service entrance cable. It also includes cast metal outlet boxes as well as conduit bodies and covers.[/FONT]

[FONT=Verdana,Arial][FONT=Verdana,Arial]It excludes fittings, boxes, or enclosures that are used in Class I, Division 1; Class II, Division 1; Class III, Division 1; Class I, Zones 0, 1, or 2; and Class II, Zones 20, 21, or 22. There are exceptions for fittings and enclosures that are specifically permitted by NEC.[/FONT][/FONT]
 