We have a service mounted on the outside of the bldg. and the inspector is requiring that we seal the conduit with duct seal,not sure if that's a code requirement.The other end of the pipe is located at the xfrmr. Need some help,please
230.8 Raceway Seal.
Where a service raceway enters a building or structure from an underground distribution system, it shall be sealed in accordance with 300.5(G). Spare or unused raceways shall also be sealed. Sealants shall be identified for use with the cable insulation, shield, or other components.
300.5(G) to seal against moisture.
(G) Raceway Seals. Conduits or raceways through which moisture may contact live parts shall be sealed or plugged at either or both ends
300.5(G)
Not often an underground raceway will allow moisture to migrate through in a way that would enter and contact live parts.
I live where there are hills. If a meter socket is lower in elevation than a handhole up by the street, and the utility conduit is not properly sealed at both ends, a fountain of water can come out the socket after a heavy rainstorm. I have seen exactly that on multiple occurances. One was a gusher.
When it says moisture does it mean condensation,otherwise I'm not sure how water would come in contact with the terminations
Low humidity in the wet location conduit?
I live where there are hills. If a meter socket is lower in elevation than a handhole up by the street, and the utility conduit is not properly sealed at both ends, a fountain of water can come out the socket after a heavy rainstorm. I have seen exactly that on multiple occurances. One was a gusher.
Low humidity in the wet location conduit?
Oh, I was just trying to put words in your mouth, sorry. I was wondering if you could state that an underground (wet location) conduit (with water in it, as always happens), would not contain enough humidity to allow moist air to reach the live parts.Wouldn't that actually draw moisture into the conduit instead of to the live parts?
300.5(G)
Not often an underground raceway will allow moisture to migrate through in a way that would enter and contact live parts.
I live where there are hills. If a meter socket is lower in elevation than a handhole up by the street, and the utility conduit is not properly sealed at both ends, a fountain of water can come out the socket after a heavy rainstorm. I have seen exactly that on multiple occurances. One was a gusher.
Sending duct seal to BP maybe it will work
230.53 Raceways to Drain.
Where exposed to the weather, raceways enclosing service-entrance conductors shall be suitable for use in wet locations and arranged to drain. Where embedded in masonry, raceways shall be arranged to drain.
It is hard to drain a raceway fast enough in your situation to keep the water out of the meter. Backflow devices will not work with the conductors in the way:grin: