Seals in conduit entering enclosure in class 1 div 1

Status
Not open for further replies.

mmorg

New member
Location
Alaska
I have a XP enclosure in a class 1 div 1 location and it has one threaded entry (trade size 2"). I have 2 MCHL cables, single pair 16 awg.I have sealed both cable ends with TMCX fittings installed into a 2" XP GUAT with a 2" close nipple to the XP enclosure.Accordingly to article 501.15 If I am interpreting this right I can have an XP GUAT between the seals and the enclosure even if the trade size is a 2"?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You are correct as long as the fitting is the same trade size as the conduit and the seal is within 18" of the enclosure.
 