petersonra Senior Member Location Northern illinois Occupation engineer Feb 17, 2011 #2 mryan said: Should multiconductor cabels be stripped when going through seals Click to expand... An excellent question.
mryan said: Should multiconductor cabels be stripped when going through seals Click to expand... An excellent question.
LJSMITH1 Senior Member Location Stratford, CT Feb 17, 2011 #3 Are we talking about something like a 12/4 SJOW cable? Or High Voltage Cable?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 17, 2011 #4 mryan said: Should multiconductor cabels be stripped when going through seals Click to expand... Normally, yes. See 501.15(D) & (E)
mryan said: Should multiconductor cabels be stripped when going through seals Click to expand... Normally, yes. See 501.15(D) & (E)
M mryan Member Feb 17, 2011 #5 Seals Thanks for the information. It really helped. I read the article that was suggested and it explained what you said.
Seals Thanks for the information. It really helped. I read the article that was suggested and it explained what you said.