T tonype Senior Member Location New Jersey Jan 30, 2014 #1 When an SEC enters a home foundation this close to grade, does it need to be in conduit? Attachments DSCF6255.jpg 126.2 KB · Views: 0
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jan 30, 2014 #2 Hard to see in the photo but do you mean the Grounding Electrode Conductor (GEC)?
petersonra Senior Member Location Northern illinois Occupation engineer Jan 30, 2014 #3 maybe he is asking about the gray cable.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 30, 2014 #4 It appears to be subject to physical damage and will need some type of protection. See 230.50(B)(6).
T tonype Senior Member Location New Jersey Jan 30, 2014 #5 infinity said: Hard to see in the photo but do you mean the Grounding Electrode Conductor (GEC)? Click to expand... Gray cable
infinity said: Hard to see in the photo but do you mean the Grounding Electrode Conductor (GEC)? Click to expand... Gray cable
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jan 30, 2014 #6 Ah now I see it. :ashamed1: I looked before with a smaller monitor and missed it off to the right. If it's not subject to physical damage it does not require protection.
Ah now I see it. :ashamed1: I looked before with a smaller monitor and missed it off to the right. If it's not subject to physical damage it does not require protection.