Having some grey area with my inspector in CO on sizing service entrance conductors from a 320A continuous / 400A max meter socket > 300A Service Entrance Rated ATS > 225A load center. Question is sizing based on 300A ATS or 225A load center. Because I'm only feeding a 225 amp main breaker, that should be what determines my wire size, not the maximum rating my equipment, correct? The code says in [230.42] "Service Entrance Conductors shall have an ampacity of not less than the maximum load to be served." That should be the 225A load center breaker and not that it passes through a 300A ATS, right? Section [310.12] also goes into services for homes and gives a table that says that you use 3/0 copper for a 225 amp service. Simply put, thanks for confirming size of service entrance conductors from meter socket to the 300A ATS, and then service entrance conductors from the 300A ATS to the 225A load center. THX.