I am attempting to size SE conductors per 220.87. It would appear that to do this the combined ratings of my 6 service disconnects could not exceed the rating of the SE per 230.90. Can i use 230.90 ex. no. 3 to get around this, considering my "calculated load" to be the (max demand over a 1 yr period@ 125%)+ new load? 220.87(3) refers me to 230.90 for service overcurrent protection. Seem to be going in circles