anyone got a different answer?
what number did you use for k?
Find out if the equipment has a switch on it or is auto adjusting to run on 208~240.
10.8..........
10.8..........
Where does that come from?
If I do it manually(using uncoated Cu): R x CM / 1000= K
.308 x 41740 / 1000=12.86 K![]()
I looked in several books that I keep on hand andK varies with temperature. 10.5 at 25C to 12.8 at 75C.
anyway, the point is moot...just got an email that the calculated load is actually 16A...so now we are at #1....
emahler said:the distance is 650+/-
OK, so now your looking at about 2000' of 1 AWG copper and 650' of 1.25" EMT. (250.122(B) requires the EGC for this circuit to be 1 AWG unless you choose to use the conduit as ground)
IMO you should start thinking about other options, I don't know pricing, but you sure do. Is all that copper and pipe going to cost less then two - 2.5 KW transformers, say 120 x 480 (or 600) and 650' of 3/4" and some 10 or 12 AWG?
actually, a quick punch into Celtic's posted calculators, at 277V i still need a #4 and at 480V we still need a #6....
not sure if it would be much of a savings....
Then I think your doing it wrong. :smile:
16 amps at 120 volts is 1.92 KW
1.92 KW at 480 is 4 amps.
I doubt very much that you need a 4 AWG to carry 4 amps @ 480 volts 650'. :smile: