Responded to a call last week where lady had stepped in to shower and was electricuted. I reported to the home and started my check list of usual culprits.
A. Checked to see if water ground was present.
No.
B. During visit, I took a screw driver, wetted the groud near the service, stab the screwdriver into the ground and tested voltage between the spicket and the ground. 0 volts. Nothing.
C. Next, I inspected the fuse box and disconnects. All was well. No appearent problems. Black to Black , Red to Red and White to White. All fused.
checked water heater. Looked new, connections were black to black, red to red and white to ground.
D. Tried to get lady to recreate the exact conditions for which she was shocked. Cut on a few lights here and there. Cut on coffee maker, and things that may be on at 7:30 am, during the time of incident. No luck recreating this.
E. Looked into the meter of the home, it looked fine. There was a top meter being used and a second meter slot that was capped off. Nothing funny, tests worked out ok. Walked over to tub, turned the tub on and let in run for 10 minutes with my foot in tub, to indirectly showing her that her cheese has fallen off of her cracker. With my foot still in tub after 10 minutes and leaving it in the tub for 5 more minutes, things were about to change. While explaining to the lady that I feel I have fixed her problem, ZZZZZZZZZZZZZZZZZZZZZZZ, I got my *** knocked off by a surge in the water. This only happened 15 minutes into the experiment.
Ah ha!!! I found the problem. Lets see if someone can figure this out? The first correct answer wins. Not sure what you win, but you win.
[ April 22, 2005, 11:54 PM: Message edited by: aelectricalman ]
A. Checked to see if water ground was present.
No.
B. During visit, I took a screw driver, wetted the groud near the service, stab the screwdriver into the ground and tested voltage between the spicket and the ground. 0 volts. Nothing.
C. Next, I inspected the fuse box and disconnects. All was well. No appearent problems. Black to Black , Red to Red and White to White. All fused.
checked water heater. Looked new, connections were black to black, red to red and white to ground.
D. Tried to get lady to recreate the exact conditions for which she was shocked. Cut on a few lights here and there. Cut on coffee maker, and things that may be on at 7:30 am, during the time of incident. No luck recreating this.
E. Looked into the meter of the home, it looked fine. There was a top meter being used and a second meter slot that was capped off. Nothing funny, tests worked out ok. Walked over to tub, turned the tub on and let in run for 10 minutes with my foot in tub, to indirectly showing her that her cheese has fallen off of her cracker. With my foot still in tub after 10 minutes and leaving it in the tub for 5 more minutes, things were about to change. While explaining to the lady that I feel I have fixed her problem, ZZZZZZZZZZZZZZZZZZZZZZZ, I got my *** knocked off by a surge in the water. This only happened 15 minutes into the experiment.
Ah ha!!! I found the problem. Lets see if someone can figure this out? The first correct answer wins. Not sure what you win, but you win.