ShockedMonkey
- North SF Bay Area, CA
So I just watched Mike's DVD and am unsure of the code's intent with regard to T450.3(B)
Based on Table/DVD example:
75 KVA xformer delta/wye 3Ph 120/208vac secondary (480v Delta primary)
75,000/360v = 208.3 amps
208 amps x 125% = 260.4 amps i.e. have to jump to a 300 amp breaker in the 208 PB
conductors sized at 300 Amps 75c= 350KCM (seems crazy overkill to me if I only need a 225 amp panel installed)
1. Now my question does the code allow (and if so where) for the following example:
75 KVA xformer (same as above ex.)
120/208v Panelboard Calculated load (incl continuous loads etc) total = 180 Amps
180 Amps X 125% = 225 amps
conductors at 75C = 4/0 secondaries to the same 75KVA xformer
Thank you.
Thank you.