hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 75kVA transformer primary 480V to secondary 208/120V three phase. The secondary conductors have 200% neutral so I have 5 secondary conductors. The secondary panelboard is within 10 feet of transformer and rated 225A with 225A main breaker.
The secondary conductors are THHN 90 degree and terminals are 75 degree.
So now the secondary conductor size more than three current carrying ampacity correction factors would apply but not sure how to check secondary conductor ampacity.
Right now plans show 5-400kcmil Al (3 phase and 2 neutrals) secondary conductor.
Questions:
1. How would this work do I first need to take a look at 75 degree column 400 kcmil AL ampacity is 270A and then take a look at 90 degree column and 400 kcmil Al ampacity is 305A and then apply more than 3 current carrying conductor factor which 305x0.8 = 244A. Since 244A is less than 270A 400 kcmil is ok?
2. If not then exactly what is the correct method of checking?
3. 5-400 kcmil correct size with more than 3 current carrying conductor factor and 90 degree THHN cable with 75 degree termination?
The secondary conductors are THHN 90 degree and terminals are 75 degree.
So now the secondary conductor size more than three current carrying ampacity correction factors would apply but not sure how to check secondary conductor ampacity.
Right now plans show 5-400kcmil Al (3 phase and 2 neutrals) secondary conductor.
Questions:
1. How would this work do I first need to take a look at 75 degree column 400 kcmil AL ampacity is 270A and then take a look at 90 degree column and 400 kcmil Al ampacity is 305A and then apply more than 3 current carrying conductor factor which 305x0.8 = 244A. Since 244A is less than 270A 400 kcmil is ok?
2. If not then exactly what is the correct method of checking?
3. 5-400 kcmil correct size with more than 3 current carrying conductor factor and 90 degree THHN cable with 75 degree termination?