what is the minimum size 75 C transformer secondary conductor, not over 3m long for a 480 volt primary to 208 volt secondary transformer supplied by a 200 ampere primary overcurrent device? i am having trouble with the calculation, i do not understand 240.22 help please
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I would say #8 based on 240.21(C)(2)-{4} ('08 Code)

but I wouldn't take that answer to the bank :)


200 x 480/208 =461/10 = 46
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Gus,
With the information given, I believe you have the correct answer, but you do have to make the assumption that the load is 46 amps or less.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Don, I was going on his question of minimum, but yes, I agree that answer would definitely be load dependant. In the real world, I have failed to ever question minimum as most installations have "load" as the determining factor, as you kmow.
Truthfully, had he not asked, I would have never thought "minimum". Bad for an inspector, but true.
 