riverjig87
Member
- Location
- Minot, North Dakota, USA
I have a utility transformer (500KVA- 480Y secondary) outdoors being fed from the utility pole. The secondary of the utility transformer feeds a CT Enclosure which is mounted within 30' and within sight of the transformer. (ALL OUTDOORS). From this CT enclosure, we are being instructed to use it as a tap for (2) 400A disconnects. According to 240.21 (C)(4), the secondary conductors from the transformer must "Terminate at a single circuit breaker (or a single set of fuses) that limit the load to the ampacity of the conductors". we meet the
According to the engineer, this CT Enclosure is "service rated" which allows this configuration to be installed in this manner. However, I do not see where this could be acceptable according to the NEC.
240.21(C)(1) does not apply being that the secondary is Y and not delta.
I would appreciate any input on this subject.
Thanks everyone.
According to the engineer, this CT Enclosure is "service rated" which allows this configuration to be installed in this manner. However, I do not see where this could be acceptable according to the NEC.
240.21(C)(1) does not apply being that the secondary is Y and not delta.
I would appreciate any input on this subject.