Secondary conductors not over 25 ft long

Status
Not open for further replies.

raider1

Senior Member
Staff member
Location
Logan, Utah
The biggest difference is that 240.21(C)(3) permits the secondary conductors to terminate at multiple overcurrent devices where 240.21(C)(6) requires that the secondary conductors terminate in a single overcurrent device.