Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
Business want me to upsize to a 500 KVA delta delta 4800 volt primary to 480 volt secondary
This secondary supply Feeder size was calculated at 505.35 amperes based on 1.25% of largest FLA motor plus 100% of FLA if remaining motors
Boss wants to use 4/0 conductor thinking he can split 500 amperes between legs of transformer each around 250 amperes (not paralleling) to motor loads
Doesn’t legs on delta need to be rated for 500 amperes each? Since same current is total on both legs push and pull per phase?
Thanks
This secondary supply Feeder size was calculated at 505.35 amperes based on 1.25% of largest FLA motor plus 100% of FLA if remaining motors
Boss wants to use 4/0 conductor thinking he can split 500 amperes between legs of transformer each around 250 amperes (not paralleling) to motor loads
Doesn’t legs on delta need to be rated for 500 amperes each? Since same current is total on both legs push and pull per phase?
Thanks