Secondary feeder Sizing conductor from transformer

Status
Not open for further replies.

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Business want me to upsize to a 500 KVA delta delta 4800 volt primary to 480 volt secondary

This secondary supply Feeder size was calculated at 505.35 amperes based on 1.25% of largest FLA motor plus 100% of FLA if remaining motors

Boss wants to use 4/0 conductor thinking he can split 500 amperes between legs of transformer each around 250 amperes (not paralleling) to motor loads

Doesn’t legs on delta need to be rated for 500 amperes each? Since same current is total on both legs push and pull per phase?

Thanks
 
Also I calculated feeder OCPD at 700 amperes based on

The largest OCPD ampacity plus the sum of the remaining FLC amperes of the remaining motors then multiplying figure at 300% for non time delay fuse at 700 amperes next lower standard size fuse for feeders from initial 722.35 ampere total load
 
Difficult to confirm without details but if you have a 3 phase load of 500 amps that would require conductors rated at 500 amps on each phase.
 
Difficult to confirm without details but if you have a 3 phase load of 500 amps that would require conductors rated at 500 amps on each phase.

In other words line 1 would need to be rated for 500 amperes and line 2 at 500 amperes as well as 500 amperes so 4/0 conductor won’t suffice?
 
Also I calculated feeder OCPD at 700 amperes based on

The largest OCPD ampacity plus the sum of the remaining FLC amperes of the remaining motors then multiplying figure at 300% for non time delay fuse at 700 amperes next lower standard size fuse for feeders from initial 722.35 ampere total load
Conductors are typically sized based on their loading. OCPD are chosen based on selected conductors.

Why are you using non time delay fuses?
 
Here’s pic of what I propose
 

Attachments

  • image.jpg
    image.jpg
    1.3 MB · Views: 3