We have several large AC and DC drive systems in our plant. I recently upgraded the service for a 150HP DC drive that was upsized to a 200HP. In the process I discovered the wye secondary of the drive isolation transformer was not grounded or bonded at the XO. The XO was left unconnected. I bonded the XO on the larger transformer that I installed, in particular because it reduced the arc flash calculation(I'm not sure why). I have since found other installations on other large drive systems installed the very same way. Everything I read online says to ground this secondary for two reasons: 1) eliminate common mode noise in both directions to or from the power system to the drive, or vice-versa. 2) localize all high frequency ground currents generating from the high speed semiconductor switching. So why would someone intentionally leave these isolation transformer secondardies ungrounded?