I have an application where we will be installing a 1.5MW 480V backup gen-set which will be connected to a 480V-4.16kV step-up transformer in order to supply backup power to a 4.16KV SWGR lineup through an existing 4.16kv breaker. The gen-set will have a breaker as well as a switchboard on the LV side of the step-up transformer where the gem-set will connect.
With this arrangement would there be a requirement for a secondary MV fused switch on the secondary of the transformer other than the breaker at the switchgear which it is feeding?
Furthermore this gen-set is being added to an already existing backup system which consists of a backup utility transformer with 4.16kv secondary and a 4.16kv fused switch which then feeds into the 4.16kv swgr breaker referenced above. The idea when adding the gen-set would be to connect the gen-set transformer secondary to the line side of the existing utility transformer secondary switch (Kirk key gen-set breaker and utility switch) and utilize the existing feeder cable between the utility transformer secondary switch and the switchgear.
For this arrangement would the existing switch be able to serve as any required secondary protection for the new step-up transformer? Are there any tap rules that would come into play with taping this seconds gen-set feed onto an existing feeder?
With this arrangement would there be a requirement for a secondary MV fused switch on the secondary of the transformer other than the breaker at the switchgear which it is feeding?
Furthermore this gen-set is being added to an already existing backup system which consists of a backup utility transformer with 4.16kv secondary and a 4.16kv fused switch which then feeds into the 4.16kv swgr breaker referenced above. The idea when adding the gen-set would be to connect the gen-set transformer secondary to the line side of the existing utility transformer secondary switch (Kirk key gen-set breaker and utility switch) and utilize the existing feeder cable between the utility transformer secondary switch and the switchgear.
For this arrangement would the existing switch be able to serve as any required secondary protection for the new step-up transformer? Are there any tap rules that would come into play with taping this seconds gen-set feed onto an existing feeder?