Secondary service conductors - Underground ductbank

Status
Not open for further replies.

designer82

Senior Member
Location
Boston
So I know primary underground service conductors are always run in concrete ductbank since this is a poco requirement. However, on every project I see the secondary service conductors are always run in underground ductbank as well.

The NEC doesn't require this for the secondary service conductors, from what I understand it allows just direct buried conduit. So how come almost all projects are showing ductbank for these?

Thanks
 
The NEC does not "require" encasement but many utilities and owners prefer it for mechanical protection of the secondary conduits. There are also depth-of-cover issues that must be considered where it is cheaper to cover the ducts in concrete than dig deeper. Be careful though because the commonly used flowable air-entrained concrete has a poorer thermal resistance than all the cable ampacity tables assume.
 
..... Be careful though because the commonly used flowable air-entrained concrete has a poorer thermal resistance than all the cable ampacity tables assume.

This is a good point. We typically use Fluidized Thermal Backfill (FTB) for our ductbank as it has a known resistivity, and we can calculate the ampacity based on the specific geometry.
 