Hi everyone,
I have moved into a new jurisdiction to serve as an inspector/plans examiner/building official (about 750 miles from where I was living) and am learning about "how things are done" in this new area. After performing an electrical inspection, I headed back to my office. On the way back, I came to a stop sign and was surprised at what I saw (picture is attached). To make a long story short, a pad mount transformer sits on a property. From the pad mount transformer, the secondary is run in about 15' of conduit and is duct taped to the top of a palm tree. From that point, it crosses over the driveway of the property, rubs underneath of a large oak tree branch, and then is duct taped to the top of another palm tree at a height of about 27', and is then run back down again in conduit. From this point, the conductors are terminated in a ground level box and run to the meter enclosure. This work was done by the utility company and was considered an emergency repair four weeks ago. No one is living in either home affected by this condition.
I immediately stopped in and called the utility company to disconnect the power due to an unsafe condition. When the utility company showed up, I was given the "we've been doing it this way for thirty years speech" and the "are you telling me that we also need do disconnect every house in this community that is done like this" and the "we're just trying to keep these contractors working so they can feed their families" speeches, which I have little use for when work is done in this manner. One of the linesman got on the phone to his boss while I was taking to the other linesman and describing what was wrong with the installation. After the other guy was done talking to his boss, he informed me that his boss said "the inspector has no business inspecting anything we do because we are a public utility, he belongs inside the house inspecting the electricians wiring". This is fine, it's not my first run in with a utility company, and I let it roll, figuring I would talk to this guys boss when I got back to my office. The linesman I was talking to said there is no danger if something were to happen since the transformer comes with a 3amp bayonet fuse to protect against any faults on the primary and secondary. I asked how does he figure that one? No path (other than the grounded conductor) back to the transformer, and I tried to explain that the bayonet fuse protects on the primary side against any internal faults to help reduce the chances of the transformer exploding, and it would protect against line surges as well. We go round and round for a few minutes with no positive results. I go back to my office, call the guys boss (Line Supervisor) and leave a message. He doesn't call me back at all which is not surprising.
I then call the Public Utility Service Commission and ask if they regulate electric co-op's and they say no and give me a number to call the Office of Regulatory Staff (ORS). The ORS were actually very pleasant to speak with and tell me that they have no governance over a co-op and that a co-op is self regulating and has their own by-laws and basically receives no oversight from any type of governmental agency. The guy from the ORS said he was going to speak with their attorney on staff and a few other internal staff members to see if they can help point me in a better direction. The guy from the ORS called me back and left a message stating he is still looking into it, but doesn't have any help as of yet. From my past experience utility companies use the IEEE NESC as their installation manual, and I no longer have access to one. I can take a bet and say this is not considered an emergency, nor a safe installation. I ordered a copy this Standard and will have it tomorrow.
I inform my boss the next day of what is going on. My boss calls the line supervisors boss and asks when this will be fixed. He informs my boss that it will be at least another two weeks. My boss says ok, and that is it. He basically told me to let it ride, which I have a hard time doing.
I do not have much experience with utility distribution, but I can make some assumptions. The first assumption would be that the 3amp fuse in the transformer protects only the primary side. If a fault were to occur on the secondary, the fuse would not trip. Am I correct in this? If I am incorrect, then I would have to then assume that either a high current from a fault condition on the secondary, will also induce a high enough current on the primary windings to trip the primary fuse, but my guess is that it would take a substantial amount of current flow on the secondary to active the primary side fuse. If this is the case, would someone be able to show me the calculation for determining this, based on assumptions of typical transformer impedance etc
A second question would be, if there is a fault on the secondary, what would have to happen to clear the fault and how much current would it take? The linesman I spoke with said the primary is 14.4KVA. I am not familiar with utility transformers, but I have never heard of a 14.4KVA stepped down to 120 in a single pad mount transformer. The transformer dimensions are about 3'x3'x3'.
A third question is, with no support from my boss, and little response from anyone, what suggestions would anyone have? The area I work is also filled with extremely wealthy people, who are able to buy 3 million dollar homes with cash. The reason I say this is because the board members have little concern about the building department. This is also a higher foot traffic area so safety is a pretty big concern. We are also in a 147 mph wind zone and seismic design category D2, which means very bad and we just started hurricane season, so it makes me nervous.
Any suggestions would be greatly appreciated.
Jake
I have moved into a new jurisdiction to serve as an inspector/plans examiner/building official (about 750 miles from where I was living) and am learning about "how things are done" in this new area. After performing an electrical inspection, I headed back to my office. On the way back, I came to a stop sign and was surprised at what I saw (picture is attached). To make a long story short, a pad mount transformer sits on a property. From the pad mount transformer, the secondary is run in about 15' of conduit and is duct taped to the top of a palm tree. From that point, it crosses over the driveway of the property, rubs underneath of a large oak tree branch, and then is duct taped to the top of another palm tree at a height of about 27', and is then run back down again in conduit. From this point, the conductors are terminated in a ground level box and run to the meter enclosure. This work was done by the utility company and was considered an emergency repair four weeks ago. No one is living in either home affected by this condition.
I immediately stopped in and called the utility company to disconnect the power due to an unsafe condition. When the utility company showed up, I was given the "we've been doing it this way for thirty years speech" and the "are you telling me that we also need do disconnect every house in this community that is done like this" and the "we're just trying to keep these contractors working so they can feed their families" speeches, which I have little use for when work is done in this manner. One of the linesman got on the phone to his boss while I was taking to the other linesman and describing what was wrong with the installation. After the other guy was done talking to his boss, he informed me that his boss said "the inspector has no business inspecting anything we do because we are a public utility, he belongs inside the house inspecting the electricians wiring". This is fine, it's not my first run in with a utility company, and I let it roll, figuring I would talk to this guys boss when I got back to my office. The linesman I was talking to said there is no danger if something were to happen since the transformer comes with a 3amp bayonet fuse to protect against any faults on the primary and secondary. I asked how does he figure that one? No path (other than the grounded conductor) back to the transformer, and I tried to explain that the bayonet fuse protects on the primary side against any internal faults to help reduce the chances of the transformer exploding, and it would protect against line surges as well. We go round and round for a few minutes with no positive results. I go back to my office, call the guys boss (Line Supervisor) and leave a message. He doesn't call me back at all which is not surprising.
I then call the Public Utility Service Commission and ask if they regulate electric co-op's and they say no and give me a number to call the Office of Regulatory Staff (ORS). The ORS were actually very pleasant to speak with and tell me that they have no governance over a co-op and that a co-op is self regulating and has their own by-laws and basically receives no oversight from any type of governmental agency. The guy from the ORS said he was going to speak with their attorney on staff and a few other internal staff members to see if they can help point me in a better direction. The guy from the ORS called me back and left a message stating he is still looking into it, but doesn't have any help as of yet. From my past experience utility companies use the IEEE NESC as their installation manual, and I no longer have access to one. I can take a bet and say this is not considered an emergency, nor a safe installation. I ordered a copy this Standard and will have it tomorrow.
I inform my boss the next day of what is going on. My boss calls the line supervisors boss and asks when this will be fixed. He informs my boss that it will be at least another two weeks. My boss says ok, and that is it. He basically told me to let it ride, which I have a hard time doing.
I do not have much experience with utility distribution, but I can make some assumptions. The first assumption would be that the 3amp fuse in the transformer protects only the primary side. If a fault were to occur on the secondary, the fuse would not trip. Am I correct in this? If I am incorrect, then I would have to then assume that either a high current from a fault condition on the secondary, will also induce a high enough current on the primary windings to trip the primary fuse, but my guess is that it would take a substantial amount of current flow on the secondary to active the primary side fuse. If this is the case, would someone be able to show me the calculation for determining this, based on assumptions of typical transformer impedance etc
A second question would be, if there is a fault on the secondary, what would have to happen to clear the fault and how much current would it take? The linesman I spoke with said the primary is 14.4KVA. I am not familiar with utility transformers, but I have never heard of a 14.4KVA stepped down to 120 in a single pad mount transformer. The transformer dimensions are about 3'x3'x3'.
A third question is, with no support from my boss, and little response from anyone, what suggestions would anyone have? The area I work is also filled with extremely wealthy people, who are able to buy 3 million dollar homes with cash. The reason I say this is because the board members have little concern about the building department. This is also a higher foot traffic area so safety is a pretty big concern. We are also in a 147 mph wind zone and seismic design category D2, which means very bad and we just started hurricane season, so it makes me nervous.
Any suggestions would be greatly appreciated.
Jake