jwatts
Member
- Location
- Chicago, IL
Doing a job where the engineer has a 150kva 480/120-208v transformer being fed with a 250amp breaker in the distribution panel adjacent to the transformer. The secondary side then shows a 400amp disconnect fused at 300amps feeding a 400amp MLO panel. First, the 150kva transformer is only rated at 180amps @480v so I am not sure why there is a 250 amp breaker. My question is whether or not a fused disconnect is required on the load side of the transformer. Would a nonfused 400amp disconnect suffice since I am feeding a 400a MLO panel? Or according to the table in NEC2011 450.3(B), if I were to install a 225amp breaker, I would not need a load side disconnect because the OCPD would be equal to 125% of the rated input current. I am not certain I am interpretting the code correctly.