H Hendrix Senior Member Location New England Nov 18, 2010 #1 Can the secondary cables go inside a building and up through the first floor to a disconnect or do they have to be run outside the building. This is a 1000a service.
Can the secondary cables go inside a building and up through the first floor to a disconnect or do they have to be run outside the building. This is a 1000a service.
R RUWired Senior Member Location Pa. Nov 18, 2010 #2 They can be run through the building but you would have to comply with article 230.6 and encase the conduit/s with 2" of concrete.
They can be run through the building but you would have to comply with article 230.6 and encase the conduit/s with 2" of concrete.
H Hendrix Senior Member Location New England Nov 18, 2010 #3 RUWired said: They can be run through the building but you would have to comply with article 230.6 and encase the conduit/s with 2" of concrete. Click to expand... Thank You.