Good afternoon all. I'm working with a solar company to provide anfld facilitate the service tie in/switch portion of the project
I had a question maybe some other experience guys here could clarify.
When designing a PV system to tie into an existing structure. Let's say for instance the existing structure has a property line box fed from the utility.
From said property line box there is one set of 500 MCM copper feeding the structure.
If the solar engineer is requiring a 400am service switch and meter for the PV system it is my understanding that you cannot just tie into the existing set of 500s as it would be overloaded.
am I wrong for thinking this way? Basically my question is does the PV system need to go directly to the utility and not tap the existing service entrance conductors?
I would say if the service entrance conductors that are existing from property line box to structure were rated for 800 amps you would be able to tie into it anywhere?
Sent from my SM-S906U using Tapatalk
I had a question maybe some other experience guys here could clarify.
When designing a PV system to tie into an existing structure. Let's say for instance the existing structure has a property line box fed from the utility.
From said property line box there is one set of 500 MCM copper feeding the structure.
If the solar engineer is requiring a 400am service switch and meter for the PV system it is my understanding that you cannot just tie into the existing set of 500s as it would be overloaded.
am I wrong for thinking this way? Basically my question is does the PV system need to go directly to the utility and not tap the existing service entrance conductors?
I would say if the service entrance conductors that are existing from property line box to structure were rated for 800 amps you would be able to tie into it anywhere?